T tonype Senior Member Location New Jersey Feb 4, 2017 #1 ...can a cable be routed behind vinyl siding? Attachments DSCF1836.jpg 115.7 KB · Views: 0
Smart $ Esteemed Member Location Ohio Feb 4, 2017 #2 As best I can tell, no section specifically prohibits doing so. There's... 300.4 Protection Against Physical Damage. Where subject to physical damage, conductors, raceways, and cables shall be protected. (A)... Click to expand... ...then nothing specific in the subsections. For NM cable, there's protection requirements for exposed work in 334.15... but behind vinyl siding is not exposed work.
As best I can tell, no section specifically prohibits doing so. There's... 300.4 Protection Against Physical Damage. Where subject to physical damage, conductors, raceways, and cables shall be protected. (A)... Click to expand... ...then nothing specific in the subsections. For NM cable, there's protection requirements for exposed work in 334.15... but behind vinyl siding is not exposed work.
T texie Senior Member Location Fort Collins, Colorado Occupation Electrician, Contractor, Inspector Feb 4, 2017 #3 In my view this not an NEC issue. I think NFPA 780 would be the direction for this.
N north star Senior Member Location inside Area 51 Feb 6, 2017 #4 $ ~ $ In the `14 Edition of NFPA 780, Section 4.18.1.1 allows it to be concealed as in the picture. $ ~ $
$ ~ $ In the `14 Edition of NFPA 780, Section 4.18.1.1 allows it to be concealed as in the picture. $ ~ $