In 2019, my company lost 13 Allen-Bradley 5069-IF8 analog input modules over the course of several months. These losses always corresponded to lightning activity in the area (a common issue here in south Florida), but often did not correspond to direct hits on the facility or the loss of any other equipment. A few times we lost one or two transmitters as well when the strikes were more direct. All panels have upstream surge protection, so I think it's fairly clear the lightning was inducing surges from the field side, even when occurring over half a mile away. I was convinced these modules had a design flaw that was allowing this to happen so easily. Since that period time I've installed Phoenix Contact analog surge protectors on each AI circuit (part number 2906767). This completely solved the issue until last month, when we lost an additional module that had the field-side protection. Again, no other device was damaged. These SPDs are expensive, and it roughly doubles the IO cost for analog inputs if I were to bake the cost in to future designs. The protection is also not as complete as I thought since it happened again, although the failure rate is vastly improved. Has anyone experienced a similar issue or have any insight into this problem?