rick hart
Senior Member
- Location
- Dallas Texas
There is a church, built late 1990 that has been struck at least three times causing damage to equipment but, not any to the building or 1600A fusable, six switch service entrance. The building is wood frame, on slab in the highesty point in the county. The EGC (at least a 2/0 cable is visible as it goes into the attic. I have not taken the panels off to see if this is the only EGC of if one also is in the slab.
A Franklin type lightning arrestor system is installed but it does not appear to be bonded to the Equipment Grounding Electrode. Their cable is bonded to a #6 copper ground for the phone utility. I did not see any bond between the phone an electric service.
This building has a good quality 4 wire fused TVSS on the service entrance. The fuses never blow on the TVSS, the fuses in the switch board don't blow BUT fuses down stream from the service for A/C controls, smoke beam detectors and electronics are hit hard.
I noticed that the computer network patchbay, DSL modem and Fire control ( about 100 feet away from the service entrance) also have a #8 solid copper ground wire attached to the cabinet but I do not see where this was grounded. Almost all damage is quite a distance from the electrical service but nothing burned or missing.
Questions:
1. The lightning system and the service entrance need to be bonded together?
2. The phone, data hub, fire alarm ground need to go to the service entrance rather than "pick up a ground somewhere" that we see all too often
3. With fuses blowing away from the service entrance, does that indicate that the surge current is coming from somewhere else. I'm thinking current swell rather that a voltage transient is causing these problems.
4. Has anyone had a similar problem that was fixed by-------?
Thanks in advance for any thoughts. I need to find the source of this damage.
A Franklin type lightning arrestor system is installed but it does not appear to be bonded to the Equipment Grounding Electrode. Their cable is bonded to a #6 copper ground for the phone utility. I did not see any bond between the phone an electric service.
This building has a good quality 4 wire fused TVSS on the service entrance. The fuses never blow on the TVSS, the fuses in the switch board don't blow BUT fuses down stream from the service for A/C controls, smoke beam detectors and electronics are hit hard.
I noticed that the computer network patchbay, DSL modem and Fire control ( about 100 feet away from the service entrance) also have a #8 solid copper ground wire attached to the cabinet but I do not see where this was grounded. Almost all damage is quite a distance from the electrical service but nothing burned or missing.
Questions:
1. The lightning system and the service entrance need to be bonded together?
2. The phone, data hub, fire alarm ground need to go to the service entrance rather than "pick up a ground somewhere" that we see all too often
3. With fuses blowing away from the service entrance, does that indicate that the surge current is coming from somewhere else. I'm thinking current swell rather that a voltage transient is causing these problems.
4. Has anyone had a similar problem that was fixed by-------?
Thanks in advance for any thoughts. I need to find the source of this damage.