I will echo Tom's advice. First check your GEC, GES, and MBJ. Make sure those connections are tight and not corroded. Most use clamps at the rod, and I would bet you can pull it apart with your hands.
Second look very closely at the CATV , Telco, antenna, and any other line protectors. They should be connected to the service GEC very close to the meter base. Again most are clamps and are loose and corroded. A big problem is you will find no line protectors, or protectors will terminate to a isolated ground rod that is not bonded to the GES, of extremely long lead lengths back to the GEC due to the communication service entering some distance from the electrical service.
As for TVSS, the best units are a collar type plugged into the meter base. Some utilities supply then with guarantees for a small monthly fee. If not check with utility as Tom suggested to see if they will allow one to be installed. 2nd best alternative is to use TVSS built into the main panel. 3rd best is a parallel unit wired into the service panel. Extreme care must be used using a parallel unit concerning lead length. Any leads longer than 6 inches makes the unit worthless. As with any TVSS unit be sure you see the UL 1449 Seccond edition rating with a SVR of 400 volts or less for 240 volt systems and 330 for 120 recepts. Avoid units that only list Joule rating, it means absolutely nothing other than junk.
Last use a quality Class ?A? device or point of use TVSS at the devices. If it is a PC make sure to select one with Telco and/or coax protectors built in.
In regard to overhead or underground service, I assume Tom is referring to the likely hood of the service being hit. Overhead is more likely to being struck by lightning as opposed to underground.
[ June 18, 2004, 09:59 AM: Message edited by: dereckbc ]