lights at stairs

Status
Not open for further replies.

southernboys

Senior Member
what nec article covers luminaries being required at stair landings. Is it just at permanent floors or landings where the stairs flip sides?
 

jwelectric

Senior Member
Location
North Carolina
Re: lights at stairs

210.70 (A) (2) Additional Locations. Additional lighting outlets shall be installed in accordance with (A)(2)(a), (A)(2)(b), and (A)(2)(c).
(a) At least one wall switch-controlled lighting outlet shall be installed in hallways, stairways, attached garages, and detached garages with electric power.
(b) For dwelling units, attached garages, and detached garages with electric power, at least one wall switch?controlled lighting outlet shall be installed to provide illumination on the exterior side of outdoor entrances or exits with grade level access. A vehicle door in a garage shall not be considered as an outdoor entrance or exit.
(c) Where one or more lighting outlet(s) are installed for interior stairways, there shall be a wall switch at each floor level, and landing level that includes an entryway, to control the lighting outlet(s) where the stairway between floor levels has six risers or more.
:)
 