gar
- Ann Arbor, Michigan
- EE
090414-1124 EST
How many feet from the transformer to the main panel. 500 ft for some of my neighbors. That is a loop length of 1000 ft. 0000 copper has a resistance of 0.05 ohms per 1000 ft. 0 copper is about 0.1 ohm/1000 ft.
Suppose the inrush is 200 A and 0.1 ohm, then we have my 20 V value calculated above. If the load is a 240 V device, then 10 V would be seen by a 120 V circuit. No change of transformer will solve this part of the problem.
The various important components needed to be evaluated for their contribution to whatever problem may exist.
My loop length is shorter and I do have 0000 copper. I have one neighbor on the transformer. I do not share service wiring with my neighbor except for about 4' from the transformer. I have light flicker from their air conditioner turning on. That is all due to transformer impedance. Some day I will determine how large a drop occurs. Should my transformer be changed? I do not think so. Our combined average load would not justify a change.
A change to a larger transformer, or a lower impedance unit, would be an un-necessary installation cost to DTE. Further a larger transformer would have higher residual losses.
I have no equipment that is adversely impacted by what limited voltage fluctations I have.