What causes the lights to dim when a large load comes on such as a ref. Or a blow dryer
The NEC's minimum requirements for service and feeder sizes we bid to get jobs.
Actually the NEC load calculations are very conservative and result in over sized services. Just look at what we install compared to what the power company connects to our service conductors.The NEC's minimum requirements for service and feeder sizes we bid to get jobs.
A lot of the dip has to do with the voltage regulation of the utility transformer. The high inrush causes a brief voltage drop. Part of the drop is in the service and branch circuit conductors, but in many cases the bigger part is in the utility transformer.Why would the lights dim if a hair dryer is turned on, even if was based on minimum code?
I thought the NEC requires the bath receptacle to be on a dedicated circuit, definitely not with light circuits. Same for ref.
And even if it wasn't, it's only a nuisance, not a hazard as long as the wires are protected by their respective ampacity breaker.
Why would the lights dim if a hair dryer is turned on, even if was based on minimum code?
I thought the NEC requires the bath receptacle to be on a dedicated circuit, definitely not with light circuits. Same for ref.
And even if it wasn't, it's only a nuisance, not a hazard as long as the wires are protected by their respective ampacity breaker.
Actually the NEC load calculations are very conservative and result in over sized services. Just look at what we install compared to what the power company connects to our service conductors.
Couldn't it also have something to do with a loose connection in the house somewhere??
POCO - 3/0 AL direct burial. EC - 3AWG THHW.
If you are talking about overhead, take a look at how much more conductors in free air can handle vs. in conduit, sheath or buried.
.