hockeyoligist2
Senior Member
- Location
- close to greenville sc
A friend called me last night, wants me to check out his mobile home service. I don't do residential work, so I don't know if this is common.
He has a 200 amp service, the well and heat pump are on breakers at the service pole. He said the well is 1 hp, 120v 50 foot run with #10, heat pump 240v #10 about three foot run. He said that they have always dimmed when either one started. He has had it for 5 years and never thought anything about it.
He had the in-laws over for Thanksgiving and his brother-in-law noticed it and said he needed to have it checked out.
Is this normal? I figured I would check the torque on the connections and check for voltage drop. Any other things I should look for?
He has a 200 amp service, the well and heat pump are on breakers at the service pole. He said the well is 1 hp, 120v 50 foot run with #10, heat pump 240v #10 about three foot run. He said that they have always dimmed when either one started. He has had it for 5 years and never thought anything about it.
He had the in-laws over for Thanksgiving and his brother-in-law noticed it and said he needed to have it checked out.
Is this normal? I figured I would check the torque on the connections and check for voltage drop. Any other things I should look for?