A troublecall today. Lights dimming and then going bright.
Pull the meter check voltage on line side. 123/v from each leg to neutral.
Plug meter in. When lights dim checked load side of meter.
100/v to neutral on one leg, 143/v to neutral on the other.
Loose neutral is what I am figuring. Maybe the connection at the service? So I check the POCO side of the connections and get the same 100/v-143/v.
I checked all other connections, nothing loose, nothing burnt.
I figured the problem must be at the pole or further. Sound right? Or would the problem still be on the HO side of the POCO connections?