When you start a large load, the high current passing through the service transformer causes a large voltage drop internal to that transformer. As a result, the voltage on the secondary of the transformer will be lower than normal. This will cause all lights (and all other loads as well) to have a lower voltage. That is why the lights go dim. Since this type of issue usually arises when a large motor is started, and since the high starting current lasts only a short time (less than one second), the resultant dimming of lights will also last a short time.
That is what is happening, but does it answer your question? If not, what type of information are you looking for? Are you trying to solve a specific problem at a specific location? There are many ways to address the problem, but they depend heavily on the type of facility, the type(s) of lighting loads, the type(s) of motors, and the nature of the service (both the transformer and the upstream grid). Could you clarify your question?