If you can, use a voltmeter to measure your 2 phases, to ground. 1st, measure with the meter out, measuring the top two lugs. You should have around 125v to ground.
Now, with the meter in place, measure the voltages. If you have a incoming neutral problem (connector, xfmr, etc...) then one phase will be somewhat higher than the other (ie: 129v and 98v).
If you find you do have this, contact your supplier, and do not unhook the ground wire anywhere in your system. Doing so will damage something, for sure!! (PS. I took out 2 tvs with the removal of 1 ground wire clamp, just 15 min. before a Super Bowl game. Man, was that a bummer, but that story can wait for a different time!!)