When that AC compressor starts it may have an instant current of over 100 amps for just a few milliseconds and then rapidly starts to drop and maybe reaches a stable current in the range of 15 to 35 amps (depending on size of unit) within a couple seconds. The larger kVA capability of the supply transformer the easier it is for it to deliver this current without a significant drop in output voltage. Size and length of conductors between the source and load will also "choke" the voltage during this short burst of current. The sag in voltage can then be followed by an overvoltage in some cases where there is poor regulation or even with a portable generator application the generator governor sees the sudden voltage drop and tries to increase engine speed and then the following sudden voltage rise goes too far because generator is now running too fast.The smaller the generator in comparison to the load the worse this effect can be.Thanks , I figured it may be voltage drop but couldn't understand why when the service was sized correctly and all branch circuits as well. So I'm assuming the utility transformer and the impedance . Thanks that makes more since.
Sent from my iPad using Tapatalk
You mean it is not from low brow installers using 14AWG....Dang!Thanks , I figured it may be voltage drop but couldn't understand why when the service was sized correctly and all branch circuits as well. So I'm assuming the utility transformer and the impedance . Thanks that makes more since.
Sent from my iPad using Tapatalk
Years ago, wired track houses. Owner complained of lights dimming when "new" refrigerator came on. Went to check it out. Yep, they dimmed. All connections good. Put amp meter on wires feeding refrigerator, 50+ amps on start up. Refrigerator turned from "new" to "just 3 years old".