Lights on 20A Circuit
augie47
Tennessee
Lack a bit of information there :D
ie: using 5 watt lamps, non-continuous you can connect 480 of them, or (1) 1500w continuous lamp..
kwired
Electron manager
NE Nebraska
lighting is usually a continuous load - so 80% of 20 is 16 amps, divide by amps per fixture to come up with how many (of the same) fixtures you can put on that circuit.
iwire
Massachusetts
Very much depends, more so today than every before.
For instance a large warehouse would have had a continuous lighting load, now most warehouses I go in have motion switching so no continuous loads.
Office buildings, again a lot of motion / occupancy / vacancy / ambient light sensors so while part of branch circuit could be continuous other parts of it not continuous.
I am not suggesting to ignore the rules for continuous loads I just think they are often over applied. No problem with that other than wasted copper. :)
iwire
Massachusetts
It shows the F1D as 120 volts and 96 watts. If it was me I would want to see a cut sheet on the fixture or the ballast cutt sheet but we will assume 96 watts is accurate.
A 20 amp 120 volt circuit can provide 2,400 watts non-continuous or 1,920 watts continuous.
That being the case 20 or 25 F1D fixtures max on a 20 amp circuit.
As a rule I don't max out my lighting circuits from the start, it is nice to have some headroom in the circuits to add fixtures if the customer feels the need to.
kwired
Electron manager
NE Nebraska
I'll just say such controls is something to consider. Every application will have different demands, many may never run for three continuous hours, yet that one activity/event every so often may have them on for much more then three hours.
iwire
Massachusetts
Read the definition of continuos load, notice they use the word 'expected'.
mstrlucky74
NJ
Great point
mstrlucky74
NJ
Thanks