Can someone help me with the calculation to figure how many lights I can put on (1) 120v 20A circuit. Thank you.
Can someone help me with the calculation to figure how many lights I can put on (1) 120v 20A circuit. Thank you.
Lack a bit of information there
ie: using 5 watt lamps, non-continuous you can connect 480 of them, or (1) 1500w continuous lamp..
lighting is usually a continuous load -
The F1D.
As a rule I don't max out my lighting circuits from the start, it is nice to have some headroom in the circuits to add fixtures if the customer feels the need to.
With LED's and 277 volt circuits, that is hardly a concern anymore.
I'll just say such controls is something to consider. Every application will have different demands, many may never run for three continuous hours, yet that one activity/event every so often may have them on for much more then three hours.Very much depends, more so today than every before.
For instance a large warehouse would have had a continuous lighting load, now most warehouses I go in have motion switching so no continuous loads.
Office buildings, again a lot of motion / occupancy / vacancy / ambient light sensors so while part of branch circuit could be continuous other parts of it not continuous.
I am not suggesting to ignore the rules for continuous loads I just think they are often over applied. No problem with that other than wasted copper.
I'll just say such controls is something to consider. Every application will have different demands, many may never run for three continuous hours, yet that one activity/event every so often may have them on for much more then three hours.
Very much depends, more so today than every before.
For instance a large warehouse would have had a continuous lighting load, now most warehouses I go in have motion switching so no continuous loads.
Office buildings, again a lot of motion / occupancy / vacancy / ambient light sensors so while part of branch circuit could be continuous other parts of it not continuous.
I am not suggesting to ignore the rules for continuous loads I just think they are often over applied. No problem with that other than wasted copper.
It shows the F1D as 120 volts and 96 watts. If it was me I would want to see a cut sheet on the fixture or the ballast cutt sheet but we will assume 96 watts is accurate.
A 20 amp 120 volt circuit can provide 2,400 watts non-continuous or 1,920 watts continuous.
That being the case 20 or 25 F1D fixtures max on a 20 amp circuit.
As a rule I don't max out my lighting circuits from the start, it is nice to have some headroom in the circuits to add fixtures if the customer feels the need to.