I went to a customer's to investigate the lights, throughout, the house "winking" when motor loads are turned on. The 240V Dryer causes the most noticeable effect. When the Disposer is turned on they "wink" just a bit. Furnace & A/C have the same effect.
The Dryer breaker is located just under the Main, A/C is just below that with the Furnace & Disposer lower in the panel.
Voltage is 125 L1 & L2 to ground. Connections tight, all bonding is in place.
With a load of 25a on one Service conductor the voltage ahead of the Main is 118, with the other at 127.5
Does anyone have any thoughts they would like to share as where check why this is happening to this extent.
I may not be explaining this very well but I hope someone can catch the drift.
Thanks