Hello everyone. I really need your help!! First of all, Id like you to know that I work as an interpreter, so I have few knowledge about electrical thing, and I'm not so good at English. Sorry for that. I appreciate it if you could advise me with using easy words. 
Is there the length limits for explosion-proof flex conduits? As far as I checked NEC2014 and NFPA 70, I found the statement about flex metallic conduit (FMC) but I could not find the specified length for explosion-proof type. Where to be installing them is classified as class 1 div1 location in Hangar, also the length of explosion proof flex conduit will be over 3m. Thank you in advance.
	
		
			
		
		
	
				
			Is there the length limits for explosion-proof flex conduits? As far as I checked NEC2014 and NFPA 70, I found the statement about flex metallic conduit (FMC) but I could not find the specified length for explosion-proof type. Where to be installing them is classified as class 1 div1 location in Hangar, also the length of explosion proof flex conduit will be over 3m. Thank you in advance.
 
				
 
 
		 
 
		 Thank for letting me know. 144in is over 3m. So over 3m explosion proof flexible couplings (conduits) exist with special order. That's good news for me