Limit Length

Status
Not open for further replies.

lmc

Member
Location
United States
I am looking to find out if there is a limit to the length of a fixture drop supported horizontally between junction box and fixture?

Thanks,
lmc
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here is the article for FMC

348.20 Size.
(A) Minimum. FMC less than metric designator 16 (trade
size 1?2) shall not be used unless permitted in 348.20(A)(1)
through (A)(5) for metric designator 12 (trade size 3?8).
(1) For enclosing the leads of motors as permitted in
430.245(B)
(2) In lengths not in excess of 1.8 m (6 ft) for any of the
following uses:
a. For utilization equipment
b. As part of a listed assembly
c. For tap connections to luminaires as permitted in
410.117(C)
(3) For manufactured wiring systems as permitted in
604.6(A)
(4) In hoistways as permitted in 620.21(A)(1)
 

electricalist

Senior Member
Location
dallas tx
Feeder Tap Rules
10-Foot Feeder Tap Rule [240.21(B)(1)]
Feeder tap conductors can be run not over 10 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 1
(1) The ampacity of the tap conductor is:
1 Not less than the computed load in accordance with Article 220, and
2 Not less than the rating of the device supplied by the tap conductors or the overcurrent protective device at the termination of the tap conductors.
(2) The tap conductors do not extend beyond the equipment they supply.
(3) The tap conductors are installed in a raceway if they leave the enclosure.
(4) The tap conductors have an ampacity of no less than 10 percent of the ampacity of the overcurrent protection device from which the conductors are tapped.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
This is the section I had rattling around in the back of my head. It does not say you have to use a factory supplied cord but it does place restrictions on having a remote j-box. In regards to the OP I guess the cord can be as long as it needs to be as long as the box is directly above the light fixture.

It does have a requirement for a strain relief, but I have no idea what the last sentence means.

410.62 Cord-Connected Lampholders and
Luminaires

(C) Electric-Discharge and LED Luminaires.
(1) Cord-Connected Installation. A luminaire or a listed
assembly shall be permitted to be cord connected if the fol-
lowing conditions apply:
(1) The luminaire is located directly below the outlet or
busway.
(2) The flexible cord meets all the following:
a. Is visible for its entire length outside the luminaire
b. Is not subject to strain or physical damage
c. Is terminated in a grounding-type attachment plug
cap or busway plug, or is a part of a listed assembly
incorporating a manufactured wiring system connec-
tor in accordance with 604.6(C), or has a luminaire
assembly with a strain relief and canopy having a
maximum 152 mm (6 in.) long section of raceway
for attachment to an outlet box above a suspended
ceiling
 