I am looking to find out if there is a limit to the length of a fixture drop supported horizontally between junction box and fixture?
Thanks,
lmc
Thanks,
lmc
Thanks,
lmc
348.20 Size.
(A) Minimum. FMC less than metric designator 16 (trade
size 1?2) shall not be used unless permitted in 348.20(A)(1)
through (A)(5) for metric designator 12 (trade size 3?8).
(1) For enclosing the leads of motors as permitted in
430.245(B)
(2) In lengths not in excess of 1.8 m (6 ft) for any of the
following uses:
a. For utilization equipment
b. As part of a listed assembly
c. For tap connections to luminaires as permitted in
410.117(C)
(3) For manufactured wiring systems as permitted in
604.6(A)
(4) In hoistways as permitted in 620.21(A)(1)
I am not using flex, using SO cord.If you mean flex than you are limited to 6'
Not supposed to do that.I am not using flex, using SO cord.
Mr. Dave will that also apply if it has a cord cap on the so ? Ive taken down hi bay lights that were that way.Not supposed to do that.
Here is the article for FMC
Factory supplied pigtail is OK. 404.XX something, something limits the use of SO in place of permanent wiring.Mr. Dave will that also apply if it has a cord cap on the so ? Ive taken down hi bay lights that were that way.
With SO it might even need a tensioner , strain relief or whatever its called the is designed to keep it from coming loose.Factory supplied pigtail is OK. 404.XX something, something limits the use of SO in place of permanent wiring.
410.62 Cord-Connected Lampholders and
Luminaires
(C) Electric-Discharge and LED Luminaires.
(1) Cord-Connected Installation. A luminaire or a listed
assembly shall be permitted to be cord connected if the fol-
lowing conditions apply:
(1) The luminaire is located directly below the outlet or
busway.
(2) The flexible cord meets all the following:
a. Is visible for its entire length outside the luminaire
b. Is not subject to strain or physical damage
c. Is terminated in a grounding-type attachment plug
cap or busway plug, or is a part of a listed assembly
incorporating a manufactured wiring system connec-
tor in accordance with 604.6(C), or has a luminaire
assembly with a strain relief and canopy having a
maximum 152 mm (6 in.) long section of raceway
for attachment to an outlet box above a suspended
ceiling