Greetings all.

Have a limit switch on a water valve with only two terminals for the switch contacts. The metal enclosure does not have a ground screw or terminal. It is an old limit switch that was connected with metallic sealtite. We have reconnected with non-metallic sealtite and the consultant has questioned that there is no ground termination. Any thoughts on what we should do.

Thanks in advance.

Stu
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
I would use a metallic raceway that's suitable as an EGC.
Yes

If the flex is necessary, I have seen a short conduit nipple on the switch, sealtite connected to short nipple, ground clamp on nipple, external bonding conductor around sealtite.

ice
 