Does NEC prevent to use certain voltage for ground mounted flood lights (serving building monument sign)?
Just for my own corusity, what do you have in mind?
(C) 277 Volts to Ground. Circuits exceeding 120 volts,
nominal, between conductors and not exceeding 277 volts,
nominal, to ground shall be permitted to supply luminaires
for illumination of outdoor areas of industrial establishments,
office buildings, schools, stores, and other commercial
or public buildings where the luminaires are not less
than 900 mm (3 ft) from windows, platforms, fire escapes,
and the like.
(D) 600 Volts
never mind the above it was a 480 volt corner grounded delta the state was talking about.
Whoops:ashamed1: