Limiters

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
So if I have 3 hots in one set and I had 5 sets would I onlyneed one limiter for all of the A phase conductors or would I need 5 separate limitersfor each A phase conductor? Either situation obviously applies to the otherphases as well. Thanks.
 

Attachments

  • Capture.jpg
    Capture.jpg
    13.4 KB · Views: 1

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Call my dumb- but what are limiters? And why use them?


Only seen limiters (not sure if these are the same) in POCO Networks- the idea is that they "fuse" open before the conductor melts since such systems requires one to burn clear for a fault.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Basically an fault in one of the parallel conductors will cause the limiter to open and not take down the entire feeder or system. The ones in the photo I posted are on the utility side of the service disconnect.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Basically an fault in one of the parallel conductors will cause the limiter to open and not take down the entire feeder or system. The ones in the photo I posted are on the utility side of the service disconnect.

Ahhh- ok.

But what stops the other conductors from over heating? Id imagine an open limited does not make itself known?
 

ron

Senior Member
Since it says to provide the limiters per the NEC ...... and the NEC does not require them, it does however permit them, do you not have to install them?

Agreed, one per individual phase conductor.
 

ron

Senior Member
Ahhh- ok.

But what stops the other conductors from over heating? Id imagine an open limited does not make itself known?
It does not make itself known when it fails, that's why I hate them.

One time I tried to monitor them, by monitoring voltage on either side, like a fuse monitor system, but it was not allowed by the jurisdiction.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Ahhh- ok.

But what stops the other conductors from over heating? Id imagine an open limited does not make itself known?

The other limiters. If you have a heavily loaded feeder running at near capacity, once one limiter opens, the others will quickly follow along.

But if a feeder has a lot of spare capacity, you might never know that a limiter is open.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Basically an fault in one of the parallel conductors will cause the limiter to open and not take down the entire feeder or system. The ones in the photo I posted are on the utility side of the service disconnect.

I thought they just protected each individual wire against overcurrent.

I guess they would also protect against a ground fault, but they would have to be installed on both ends of the feeder, right?
 