You need one limiter per phase conductor. Neutral conductors do not get limiters.
View attachment 19203
Basically an fault in one of the parallel conductors will cause the limiter to open and not take down the entire feeder or system. The ones in the photo I posted are on the utility side of the service disconnect.
It does not make itself known when it fails, that's why I hate them.Ahhh- ok.
But what stops the other conductors from over heating? Id imagine an open limited does not make itself known?
Ahhh- ok.
But what stops the other conductors from over heating? Id imagine an open limited does not make itself known?
Basically an fault in one of the parallel conductors will cause the limiter to open and not take down the entire feeder or system. The ones in the photo I posted are on the utility side of the service disconnect.