Re: Limiting 48 space panel to 42 spaces
My earlier post was wrong. It was a GE, not an Eaton panel. The panel had space for 42 circuits, plus a vertical main circuit breaker at the top and a vertical sub-feed breaker at the bottom, both connected direct to the bus. GE's fabrication facility said the sub-feed breaker used three of the allowable spaces, so the top six breaker spaces had to be blank. They did not have a good way to defeat just three spaces on a three-phase panelboard.
I believed that the 200A panel internals could handle 42 circuits. Its interior was identical to the 42 circuit MLO panels we had on the project, except for the sub-feed breaker. The panel was protected by a 150A Main CB and the typical load on each 20A CB was 500 VA . (Motor space heaters, solenoids, HVAC control power, etc.)
I have difficulty seeing where the 42 circuit limitation provides additional safety in cases like this or in other industrial situations.