fastline
Senior Member
- Location
- midwest usa
- Occupation
- Engineer
And still making no sense to me, we are having a rural electric entrance installed where the POCO has a stated limit of 10hp motors on the line yet will prove as many amps as we want. So I can get 1000A of 240/1p BUT they limit the line to 10hp motors. I have already asked about soft starts, VFDs, etc. They seem to ignore any such conversation and just say "nothing bigger than 10hp".
I have machines that are certainly bigger than 10HP and I have no choice but to do my own work to limit problems on the line and run them. I don't want to be anti-POCO but they are not making any sense to me and I would bet the EE that designs the systems knows that.
I have some machines with 15-20HP motors/VFDs. These would never start across the line. Usually 2-3sec accel rates on them. Based on some testing, I am inclined to consider the highest possible current through the VFD as the limit for a motor start. In one instance, I have a VFD that has a stated overload capacity of 120% of the 30min rating so 105A 230V/3p or 182A 230V/1p.
When I consider the inrush of a 10HP motor, the 1p FLA current should be around 55A so a hard start might be 550A.
Thoughts?
As well, I have to run rotary phase converters for now. I have a few 10HP units that I built. I tested one and got an inrush test of 128A. Now I have heard that RPCs won't have quite the inrush of a direct connected single phase motor but I will do more testing.
This brought me to my next question, if I decided to combine all my smaller RPCs into 1 bigger one, I would not want to try to start that on their line. So I was considering a pony start setup to bring the idler to full speed before energizing it. I have read where some think inrush would be a non-issue with this because the motor is already at speed BUT I know it takes a little time to magnetize the coils and produce the needed impedance. Would there be any way to determine this other than some testing?
I have machines that are certainly bigger than 10HP and I have no choice but to do my own work to limit problems on the line and run them. I don't want to be anti-POCO but they are not making any sense to me and I would bet the EE that designs the systems knows that.
I have some machines with 15-20HP motors/VFDs. These would never start across the line. Usually 2-3sec accel rates on them. Based on some testing, I am inclined to consider the highest possible current through the VFD as the limit for a motor start. In one instance, I have a VFD that has a stated overload capacity of 120% of the 30min rating so 105A 230V/3p or 182A 230V/1p.
When I consider the inrush of a 10HP motor, the 1p FLA current should be around 55A so a hard start might be 550A.
Thoughts?
As well, I have to run rotary phase converters for now. I have a few 10HP units that I built. I tested one and got an inrush test of 128A. Now I have heard that RPCs won't have quite the inrush of a direct connected single phase motor but I will do more testing.
This brought me to my next question, if I decided to combine all my smaller RPCs into 1 bigger one, I would not want to try to start that on their line. So I was considering a pony start setup to bring the idler to full speed before energizing it. I have read where some think inrush would be a non-issue with this because the motor is already at speed BUT I know it takes a little time to magnetize the coils and produce the needed impedance. Would there be any way to determine this other than some testing?