Line and Load

Status
Not open for further replies.

electricalperson

Senior Member
Location
massachusetts
dont believe so. never had any inspector tell me it was wrong when i done it. if by line and load you mean gfci wiring. if its a service you cannot put conductors off of the load side of service equipment in the same conduit as line
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
CaptainConduit said:
Is there a code requirement that says line and load wires of the same circuit can't be ran in the same conduit???

If line and load of the same circuit can not be in the same conduit we have a major problem with light switches.

Roger
 

EBFD6

Senior Member
Location
MA
The only time I have ever experienced this is with VFD's, and it is not a code issue I believe, but rather a manufacturer recomendation to keep line and load seperate.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
LarryFine said:
Then I guess we need a better definition of "line" and "load" from the OP'er.


Captain?

Larry, Line / Load is Line / Load , the application is what is needs to be defined.

Roger
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
If you mean line and load of a U.P.S.
No,Most of the time the Mfgr. prohibits it.
But as far as the N.E.C. there are a few places that prohibit it too.
 
Last edited: