flightline
A job is being proposed whereby a number of special poles are going to be installed to support some AVI [automatic vehicle identification] readers. These will be located @ 16? above the pavement. There will also be 1 or 2, 1kW HID fixtures at the top, @40?. The AVI readers will require a communications cable as well as a power supply from a power limited supply. This could be a similar condition where someone wishes to install a CCTV camera on an existing light pole as well; the conditions would be similar. Normally the fixtures operate at 480 volts, but a 120-volt supply for the pole-mounted fixtures has been chosen. The transformation is within 50?, so voltage drop is not a concern.
What is a concern, however, is NEC 410.15 (b), in that there will be ?2- different potentials within the pole. Fishing in a flexible raceway from the base to the arms is one option. For clarification, I went to the 2002 NEC Handbook; they had this passage:
n 410.15(B) metal poles are permitted to be used as a raceway. If the pole is used as a raceway, the user is reminded to maintain the required separation between power wiring and any communications, signaling, and power-limited circuits that may also be installed within the pole.
For example, where a light pole supports a luminaire and a security camera, the security camera signaling and power-limited wiring may be installed within the pole cavity. Because the pole contains open circuit conductors (e.g., THW or XHHW conductors) to supply the luminaire already, the separation requirements can be fulfilled by enclosing the camera conductors within a flexible raceway and installing that raceway within the pole. Of course, the use of a cable or cord assembly for the lighting circuit conductors remains an optional choice for the user. The provisions of 410.15(B)(6) remind the user that the conductors are to be supported in accordance with 300.19, the same as a vertical raceway.
Section 410.15(B) is not intended to necessarily require the placement of a raceway for communications cables on the exterior of a lighting pole.
Would you take this to mean, as the handbook contends, that if we were to run to 120-volt lighting circuit via an approved cable, then no raceway separation would be required, as it would have already been achieved?
(resized photo for this post, compliments of Dave Nix aka websparky)
[ September 09, 2003, 08:33 PM: Message edited by: flightline ]