Line & Load Terminals

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Where in the Code is the requirement that Line terminals must be terminated on the Line side of a breaker where so marked ??
 
Not sure that it is in the code. I think just a 110.3(B) issue.
From the UL Guide Information for "Circuit Breakers, Molded Case and Circuit-breaker Enclosures (DIVQ)"
Line and load markings on a circuit breaker are intended to limit connections thereto as marked.
 
Thanks much.
I knew I had seen the documentation and was frustrated I could not find it in the NEC
I wish my memory was as extensive as my library where I found DIVQ.
 
Top