for the life of me i cant remember how to calculate line loss
for example 6 ga CU on a 50 amp breaker , with a varying load up to 50 amps at times , making about a 500 foot run yes i know this is way way way way undersized
how would one calculate the line loss for that ?
also another question
say you have a sub with a 100 amp cb in it then the conductors feed another panel at 100 amps , then from there to another 100 amp cb when a overload condtion exist why would it trip the first 100 amp CB and not the one closest to the fault .
closest thing i could figure is the first one see's the worst of the overload first ?
for example 6 ga CU on a 50 amp breaker , with a varying load up to 50 amps at times , making about a 500 foot run yes i know this is way way way way undersized
how would one calculate the line loss for that ?
also another question
say you have a sub with a 100 amp cb in it then the conductors feed another panel at 100 amps , then from there to another 100 amp cb when a overload condtion exist why would it trip the first 100 amp CB and not the one closest to the fault .
closest thing i could figure is the first one see's the worst of the overload first ?