Line-Neutral= 120v, L-Grnd=108v?

Status
Not open for further replies.

sw_ross

Senior Member
Location
NoDak
And no continuity between Neutral and Ground?

Must be a loose connection somewhere in the EGC path...

Also, gfci doesn't trip when I short out line to ground?
 
Hook up a incandescent bulb to the line and the ground and see if the voltage disappears. You may be reading ghost voltage.
 
171016-1420 EDT

sw_ross:

What is your definition of ground and where is it?

Is it remote earth? A conductive water pipe where it enters the building? A ground rod at the rod? A screwdriver stuck in the yard outside? A conductive gas line? A conductive sewer pipe? A machine sitting on a cement floor?

.

.
 