Line reactor to small?

Status
Not open for further replies.

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Purchased an xxx VFD along with the a reactor that is to be used for a 10 HP. Line or load. We are using it on the line side.

VFD says 19 amp input, reactor says max amp of 14. O bother.

Larger reactor?
Yes, possibly. If you saturate it, you may as well not have it there.

But just because the VFD is rated for 19A doesn't mean it will draw that much. That will be determined by the LOAD. If your MOTOR is rated for 10HP, it's not likely to draw more than 14A, assuming it's a motor made in the last 20 years or so. VFD max input amps are often determined by the voltage CLASS, ie 240V or 400V CLASS, and the 400V class will often include 480V ratings. IEC kW and NEMA HP motor ratings tend to be equivalent, but because Asian and European VFD mfrs use 380-400V as a standard, their current for the same motor will be higher. Therefore, when you buy a "460V 10HP" drive from one of them, it is often MADE for a 7.5kW 380V motor, which at the equivalent mechanical HP rating, will draw more current. Hence that drive being rated for 19A instead of 14A.

And by the way, on the LINE side of the VFD, the current draw will always be LOWER than the load current, because the VFD will correct to .95 PF, so if the motor nameplate says 14A at a .8PF, that will only equate to around 12.9A input current (assuming 3% losses in the VFD).
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
My concern is more with everything on the line side being rated at 125% of the drive current rating. The motor load will lessen by about 1/3 once the VFD is installed. We are changing sheave ratios at that time.
125% per the NEC, 430.122? Remember, that's only talking about the FEEDER CONDUCTORS, nothing else.
 

LMAO

Senior Member
Location
Texas
Your VFD may have been oversized for the motor. Reactor should really be sized for motor FLA (realistically, VFD line current is always lower than motor current but that's different topic).
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Purchased an xxx VFD along with the a reactor that is to be used for a 10 HP. Line or load. We are using it on the line side.

VFD says 19 amp input, reactor says max amp of 14. O bother.

Larger reactor?

it will be fine. NEC FLA for a 480V 10HP motor is 14 Amps. That's why it says 14 Amps on it. As another poster said the VFD input current will be less than the motor current anyway, and it will probably never run at full load anyway.
 