energywork
Member
- Location
- California
- Occupation
- Technical Consultant
Hi yall, I'm working on dev-phase design for a new (400a, 208/120v 3p) electrical service in an existing multifamily building in CA (San Diego City ahj, SDGE poco). Super space-limited, electrical room is pretty full, and there are no free meter hubs, or any place to install one in existing gear/meter bank (AFAIK), so i'm wondering if it would be allowable to:
Tap the utility line-side bussing in the gear (downstream from shared disconnect, upstream from existing tenant meter bank) and run conductors to a new meter/disconnect on the adjacent wall.
Specs are: service entrance fed from UG vault transformer adjacent to electrical room; 3000A Eaton/CutlerHammer switchgear/service entrance, bussing Ys, on the left is 1000a house service switchgear section; on the right is a 2000a shared disconnect and tenant meter bank. Looks like there's more space/access on the right side of the gear, so would expect to tap on that side (probably downstream of 2000a disco/upstream of meter bank), and run conductors in rigid conduit to the adjacent wall (~10-20' horizontal, ~20-30' conductor length with ups and downs, following NEC tap rules) where we could set a new 400a meter hub/disconnect.
(looking for whether this concept is allowable in general - from an NEC and utility electric service standards POV, could this kind of configuration even get approved? if yes, i'll worry about nuts-and-bolts of bussing config and exactly where/how to tap the Eaton gear as a secondary step. any specific codes or standards you could point me to that cover this would help)
An EE already took a look at the calcs and said there was plenty of amperage capacity, and thought it would be OK per NEC, but hadn't seen this done before and didn't know if SDGE would OK it; electrical subs we've talked to have been nervous about poco approval (idk about other states, but CA utilities can be challenging to work with for anything remotely nonstandard). Closest thing I've seen are line-side-tapped output-only meters for PV systems, which in physical/electrical config are pretty similar, but here we want to install a new bidirectional meter service (to land new heat pump electric water heater and new PV+ESS; with electric rate tarriff and pv value reasons to want to do this on a new separate meter). Nobody I've spoken with has been able to confidently say that it's allowed, but nobody has been able to point me to any written rule that would disallow it either, so I'm here.
Frequent lurker and first-time poster here, so hi! and thanks in advance!
Tap the utility line-side bussing in the gear (downstream from shared disconnect, upstream from existing tenant meter bank) and run conductors to a new meter/disconnect on the adjacent wall.
Specs are: service entrance fed from UG vault transformer adjacent to electrical room; 3000A Eaton/CutlerHammer switchgear/service entrance, bussing Ys, on the left is 1000a house service switchgear section; on the right is a 2000a shared disconnect and tenant meter bank. Looks like there's more space/access on the right side of the gear, so would expect to tap on that side (probably downstream of 2000a disco/upstream of meter bank), and run conductors in rigid conduit to the adjacent wall (~10-20' horizontal, ~20-30' conductor length with ups and downs, following NEC tap rules) where we could set a new 400a meter hub/disconnect.
(looking for whether this concept is allowable in general - from an NEC and utility electric service standards POV, could this kind of configuration even get approved? if yes, i'll worry about nuts-and-bolts of bussing config and exactly where/how to tap the Eaton gear as a secondary step. any specific codes or standards you could point me to that cover this would help)
An EE already took a look at the calcs and said there was plenty of amperage capacity, and thought it would be OK per NEC, but hadn't seen this done before and didn't know if SDGE would OK it; electrical subs we've talked to have been nervous about poco approval (idk about other states, but CA utilities can be challenging to work with for anything remotely nonstandard). Closest thing I've seen are line-side-tapped output-only meters for PV systems, which in physical/electrical config are pretty similar, but here we want to install a new bidirectional meter service (to land new heat pump electric water heater and new PV+ESS; with electric rate tarriff and pv value reasons to want to do this on a new separate meter). Nobody I've spoken with has been able to confidently say that it's allowed, but nobody has been able to point me to any written rule that would disallow it either, so I'm here.
Frequent lurker and first-time poster here, so hi! and thanks in advance!