DPW
Member
- Location
- FT. SMITH, AR
My question are:
1)Does the distance from the line side OCP (overcurrent protection device) to the tap need to be included in the overall length of the tap (10ft, 25ft... limitations)?
2)If not, can the OCP device such as a MDP circuit breaker be remotely located from where the tap is made?
I have always thought that the line side OCP needed to be located in close proximity as to where the tap was made.
Any illustrations are appreciated.
REFERENCES
240.2 Definitions.
Tap Conductors. As used in this article, a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4.
240.21:
(2) Taps Not over 7.5 m (25 ft) Long. Where the length of the tap conductors does not exceed 7.5 m (25 ft) and the tap conductors comply with all the following:
(1) The ampacity of the tap conductors is not less than one-third of the rating of the overcurrent device protecting the feeder conductors.
(2) The tap conductors terminate in a single circuit breaker or a single set of fuses that limit the load to the ampacity of the tap conductors. This device shall be permitted to supply any number of additional overcurrent devices on its load side.
(3) The tap conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.
1)Does the distance from the line side OCP (overcurrent protection device) to the tap need to be included in the overall length of the tap (10ft, 25ft... limitations)?
2)If not, can the OCP device such as a MDP circuit breaker be remotely located from where the tap is made?
I have always thought that the line side OCP needed to be located in close proximity as to where the tap was made.
Any illustrations are appreciated.
REFERENCES
240.2 Definitions.
Tap Conductors. As used in this article, a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4.
240.21:
(2) Taps Not over 7.5 m (25 ft) Long. Where the length of the tap conductors does not exceed 7.5 m (25 ft) and the tap conductors comply with all the following:
(1) The ampacity of the tap conductors is not less than one-third of the rating of the overcurrent device protecting the feeder conductors.
(2) The tap conductors terminate in a single circuit breaker or a single set of fuses that limit the load to the ampacity of the tap conductors. This device shall be permitted to supply any number of additional overcurrent devices on its load side.
(3) The tap conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means.