We have a job where a roof-top HVAC unit is going to be replaced. The drawings show that we are to use the existing feeder to feed the new unit. The existing feeder is 3-#4 CU conductors, from a 3 pole 70 amp circuit breaker, into a 100 amp fused switch at the unit with 70 amp fuses. The new unit will be fused at 25 amps with a 30 amp fused disconnect. Is it ok to feed the 30 amp rated disconnect from a 70 amp breaker? I would think that the disconnect would need to be a 100 amp disconnect. I can't find it in the NEC. A couple of years ago we had an inspector make us install a disconnect with the same rating as the feeder and we ended up using fuse reducers in a similar circumstance.