M mortimer third party inspector Location New England Occupation retired Jan 30, 2019 #1 can someone give me a code ref. to the tap occurring before the main breaker?
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Jan 30, 2019 #2 2014 705.12(A), 230.40 exception 5, 230.82(6)
G ggunn PE (Electrical), NABCEP certified Location Austin, TX, USA Occupation Consulting Electrical Engineer - Photovoltaic Systems Jan 30, 2019 #3 electrofelon said: 2014 705.12(A), 230.40 exception 5, 230.82(6) Click to expand... Also pertinent is 705.31.
electrofelon said: 2014 705.12(A), 230.40 exception 5, 230.82(6) Click to expand... Also pertinent is 705.31.
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Jan 30, 2019 #4 ggunn said: Also pertinent is 705.31. Click to expand... :thumbsup: