I can be doen either way but having the load side on top can present some safety issues. You should put a warning label on the breaker stating the configuration.
I see no danger as long as qualified people are working on the equipment.
Conduit fill looks questionable but I'm sure that it's probably ok.:smile:
8 -350s and 2 grounds in a 4" close nipple, not nearly full. :smile:
The breaker will work fine feeding the load side it doesn't know the difference. I agree with the others it may be confusing but it is a code complient install.
The breaker may work fine, but the AHJ may reject the install if the breaker specs don't specifically state that reverse feeding is allowed.
He may try, but he may be challenged.The breaker may work fine, but the AHJ may reject the install if the breaker specs don't specifically state that reverse feeding is allowed.
Where is the requirement that says the breaker must allow reverse feeding? If the CB doesn't specify line/load you can use it either way.
Paragraph 9.1.1.13 reads: ?Circuit breakers shall be marked ?line? and ?load? unless the construction and the test results are
acceptable with the line and load connections reversed."
Which supports Robs point, unless it is marked line and load it is suitable for backfeed.