mkmorris
- Spartanburg, SC
- Reliability Engineer
We were having issues on a circuit last night, so we measured the line voltage upstream of the distribution panel and found the following. Apparently this has been an ongoing issue for 5 months and I am walking into it now. Line voltage measured this morning was as follows:
L1-L2: 452 VAC
L1-L3: 452 VAC
L2-L3: 456 VAC
The upstream transformer is Delta 13,200 down to Wye 480. We have a voltage drop because the 13.2kV we receive from utility is closer to 12.5kV coming in based on the taps. We hope to change the taps in time to get closer to 13.2kV when production allows us the downtime. Line to Ground was very imbalanced and I could not understand why. We have a resistive grounding system (That is in alarm), but I am not sure if that system would cause that imbalance, or if more likely there is an issue with the upstream transformer. I have not dealt with resistive grounding systems yet in life which is why I ask.
L1-G: 198.0 VAC
L2-G: 256.0 VAC
L3-G: 368.2 VAC
I cannot get the downtime to test the transformer (DLRO, TTR, DOBLE, etc). Any ideas on what may cause that line-to-neutral imbalance is greatly appreciated. Currents all seem balanced on the 480 side and upstream from the 13.2 breaker.
L1-L2: 452 VAC
L1-L3: 452 VAC
L2-L3: 456 VAC
L1-G: 198.0 VAC
L2-G: 256.0 VAC
L3-G: 368.2 VAC