Line Voltage Thermostat
A/A Fuel GTX
WI & AZ
Regarding 240V baseboard heaters, I normally use a double pole thermostat to open both lines when the set point is satisfied. I am facing a situation where the load would exceed the thermostat's rating if wired as described above. My question is, in a situation where the heating load is 8kw@240V which would translate to 33.33A, could I use a double pole thermostat rated at 25A and bring two circuits in and just break one leg of each circuit through the thermostat? One problem I can see is that I would have one thermostat being fed from two double pole breakers and I wonder if 210.4 (B) would prohibit this installation? Secondly, is it legal to break just one side of a 240V circuit as described above?
Breaking just 1 leg of a circuit that pulls 33 amps will not save a thermostat that is designed for a max of 25. The load thru it will still be 33 amps. We use a contactor(s) controled by the thermostat for this type of application. Yes, switching one line is OK for control purposes but not if the thermostat is being used as a disconnecting means.
Actually, breaking one line of a circuit that pulls 4KW would only be a load of 17A. What I meant to say was if I take a load of 8kw, break it down to 2ea loads of 4kw each and run the entire load through a single double pole thermostat but only breaking one line of each circuit through each pole of the thermostat.
As I understand the OP, he was going to use the thermostat to break one side of half the load or about 17A. The answer is use contactors as Tom said.
Would the OCPD be acceptable as the disconnecting means if it were in another area of the building?
It won't work anyway. 2-pole T-stats only open one line for temperature control. The second line opens only during 'off' operation.