J jimwalker Senior Member Location TAMPA FLORIDA Feb 20, 2006 #1 just how high can we accept a 277/480 feed from poco ? is 290/505 too high ? Will it cause electronic ballast a problem ?
ron Senior Member Location New York, 40.7514,-73.9925 Feb 20, 2006 #2 Re: Line voltage I understand that plus or minus 10% is acceptable. Your reading is approx 5%.
J jimwalker Senior Member Location TAMPA FLORIDA Feb 20, 2006 #3 Re: Line voltage Perhaps it will drop after we get a real load.Transformer only running about 10% load for a while
ron Senior Member Location New York, 40.7514,-73.9925 Feb 20, 2006 #4 Re: Line voltage Definitely when you draw more load, the internal impedance of the upstream transformer will reduce the incoming voltage.
B bcfoster Member Feb 28, 2006 #5 Re: Line voltage 290/505 is within limits and would drop as more of a actual load is placed on it. But if you still have issues with it I would contact the local poco (TECO I believe still carries all of Tampa) and ask one of their guys.