We have a Square D enclosure that has one 2000 amp breaker in it and that is the only thing in the enclsoure. Can the the line wires be connected to the bottom of the breaker and the load wires connected to the top of the breaker? Please provide where this is covered on the code.
We have a Square D enclosure that has one 2000 amp breaker in it and that is the only thing in the enclsoure. Can the the line wires be connected to the bottom of the breaker and the load wires connected to the top of the breaker? Please provide where this is covered on the code.
110.3 Examination, Identification, Installation, and Use of Equipment.
(B) Installation and Use.
Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
CIRCUIT BREAKERS, MOLDED CASE AND CIRCUIT-BREAKER ENCLOSURES (DIVQ)
....
Line and load markings on a circuit breaker are intended to limit connections thereto as marked.