liquid soap dispenser over GFCI outlets

Status
Not open for further replies.
I am having a issue with housekeeping. They keep putting liquid soap dispensers above the GFCI outlets in the restrooms. The soap drips into the outlets and it does one of two things. First, it ruins the outlet and no power is available. Second, the trip mechanism won't work. The second reason is my major concern because of the danger of electric shock.

I am having a trouble locating the part of the code that covers this. I believe it is a code violation, but I can't find it.
 

iwire

Moderator
Staff member
Location
Massachusetts
There is no NEC section regarding soap dispenser placement.

I might use 110.12(C) which prohibits electrical equipment from being contaminated with cleaners, abrasives or corrosive residues.
 

iwire

Moderator
Staff member
Location
Massachusetts
For what it is worth it may be easier to move the receptacles than trying to get housekeeping to follow the NEC. :grin:
 

brian john

Senior Member
Location
Leesburg, VA
Hey maybe house keping is just trying to keep the GFCI outlets clean. Makes it easier on them, presoaped and a little water makes for easy clean up and they are GFCI's, though hot to neutral soap shorts might caused a problem.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Dale,
Second, the trip mechanism won't work.
I expect that you mean that the test button doesn't work. Soap on the exterior should not interfere with the electronics inside.
Don
 
This is in a nursing home setting with a restroom that is shared by many individuals. The sinks with the outlets are for the patients to shave themselves with electric razor. There is not a lot of room for a mirror, sink, outlet and soap dispenser. The wall is a brick wall and we have discuss moving the outlets higher, but some of the patients are in wheelchairs. We have suggested rechargable or manual razors. We did have a situation where one outlet was full of liquid soap. One of the housekeepers threw water in it to clean it out. There were sparks, but the GFCI DID NOT trip out. At this moment, the GFCI are removed until we can decide on the safe solution.
 

brian john

Senior Member
Location
Leesburg, VA
The GFI will not trip on a phase to neutral short. Any chance they might be convinced to grow beards, very becoming on older gents, on the women that is another issue.
 

allenwayne

Senior Member
hockeyoligist2 said:

A normal homeowner will tear those up in a heart beat could you imagine in a situation as described.

Confounded new inventions !!!!! Back in my day we just hooked the wires to what we were using, sparks or no sparks :)
 
Weatherproof covers were also discussed, but we wonder would they keep the cover down like they are suppose to. If they throw water in a LIVE outlet, are they smart enough to operate a weatherproof box????
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Stick, that looks like a pretty cool product for this application. :cool:
icon14.gif


banner.png

And if it comes in pastels, I'm definutely on board! :D
 

realolman

Senior Member
Can't YOU move the soap dispenser?

I work around some dopes, (they say the same thing ) but it's hard to imagine anyone not understanding wet recepticals.
 