B bs123 Member Location Panama Oct 27, 2016 #1 Hi all, For Class 2, Division 1 and 2 areas. When using Liquid Tight Flex Conduit, are seals mandatory on the enclosure? Our raceway runs are all down and horizontal. Thanks in advance.
Hi all, For Class 2, Division 1 and 2 areas. When using Liquid Tight Flex Conduit, are seals mandatory on the enclosure? Our raceway runs are all down and horizontal. Thanks in advance.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 27, 2016 #2 Do the raceways run down for 5' or horizontal for 10'?
B bs123 Member Location Panama Oct 27, 2016 #3 don_resqcapt19 said: Do the raceways run down for 5' or horizontal for 10'? Click to expand... Yes they do.
don_resqcapt19 said: Do the raceways run down for 5' or horizontal for 10'? Click to expand... Yes they do.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 27, 2016 #4 That appears to be in compliance with 502.15.