LIQUID TITE?

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
C fitting would be my choice. But how about a ridgid coupling with 2 box connectors
Plus a reducing bushing?;) OP is changing raceway size.

There are some that will claim they are not listed for use with rigid coupling - and are probably correct, though the C body probably isn't properly supported by flexible conduit either - and still may have similar listing issues as the coupling with a fitting inserted instead of threaded RMC or IMC.
 