liquidtight conduit non metallic
Depends on what you are using it for, I think 680 -hot tubs limits you to 6 feet, and i think it's limited to 6 feet for service raceways.
Check out 356.10 and 356.12.
Type B can be longer than 6 feet if properly secured.
Typical Carflex is type B.
NO the six foot rule applies when using liquid tight metallic conduit. The metal
spiral inside the conduit can be used as your ground if you use approved
connectors & keep it six feet or less in length.
For non metallic conduit (what you are using) a ground wire is required for any
length conduit from just inches to hunderds of feet.
As I said.
If it is not type B it can't be longer than 6 feet. Yes there is the 6 foot equipment grounding rule on metallic flex, but the rule is for equipment grounding and not a limit on the length of metallic flex.
680.42(1) limits it to 6 feet for outdoor spa/hot tub installations.
230.43
(15) Flexible metal conduit not over 1.8 m (6 ft) long or liquidtight flexible metal conduit not over 1.8 m (6 ft) long between raceways, or between raceway and service equipment, with equipment bonding jumper routed with the flexible metal conduit or the liquidtight flexible metal conduit according to the provisions of 250.102(A), (B), (C), and (E)
(16) Liquidtight flexible nonmetallic conduit
(15) does have a 6 foot limit for a particular condition.
(16) does allow it with no limitation on lenght.
680.42 Outdoor Installations. A spa or hot tub installed
outdoors shall comply with the provisions of Parts I and II
of this article, except as permitted in 680.42(A) and (B),
that would otherwise apply to pools installed outdoors.
(A) Flexible Connections. Listed packaged spa or hot tub
equipment assemblies or self-contained spas or hot tubs
utilizing a factory-installed or assembled control panel or
panelboard shall be permitted to use flexible connections as
covered in 680.42(A)(1) and (A)(2).
(1) Flexible Conduit. Liquidtight flexible metal conduit
or liquidtight flexible nonmetallic conduit shall be
permitted in lengths of not more than 1.8 m (6 ft).
Not so here in CA. Has been this way for a while
Now that I reread the section it allows 6 ft outside the unit and whatever you need inside the unit so I guess its certainly concievable depending on the routing inside the tub that you could ahve alength considerably over 6 ft total. In any case a ground is required to be run no matter what.
That would make sense to me but I don't see where it says that, unless there is a change in 2011 and that is what you are looking at.
356.10 allows longer than 6' installation.
Other article may require otherwise.