The LFMC goes straight to the motor. Is there a fitting, sleeve, etc that is made for an application like this?Are there open conductors in the enclosure or does the LFMC go directly to the motor? If so it can go straight through the side of the cabinet but there should be a bushing or some other abrasion protection.
A chase nipple.The LFMC goes straight to the motor. Is there a fitting, sleeve, etc that is made for an application like this?
yes, the enclosure is a building exhaust fanIs there air flow thru the enclosure ?
Would that not make the LFMC a violation of 300.22(B)yes, the enclosure is a building exhaust fan