Liquidtight Flexible Metal Conduit

Status
Not open for further replies.

mikekski

New member
If I am using liquidtight metal conduit simply as protection for a communications circuit does it require a bonding jumper?
 
Grounding or bonding?

This is what I think you may be looking for. I may be wrong though.

250.86 Ex.#2

'05
"short sections... raceways... protection of cable assemblies from physical damage shall not be required to be connected to be grounded"

'08
"short sections... raceways... protection of cable assemblies from physical damage shall not be required to be connected to beconnected to the equipment grounding conductor"
 