Re: Liquidtight use for adjacent enclosure purge flow?
Since the potential source of ignitible material is
outside the enclosures, you are using a "pressurized" rather than "purged" system. This is a good thing.
Personally, if it had been up to me, I would not have required venting the system at all, since all that is needed is to maintain a positive pressure of 25pa (0.1 in. water) in an area where no gas is supposed to be in the first place (Definition of Div 2). 25 pa is piddlely. But it isn't up to me.
Pressurization is an identified protection technique for Class I locations (Section 500.7 via 500.2 and NFPA 496). The "catch" is that the installation is still
in a Division 2 location and nothing in 501.4 recognizes pressurization for wiring methods as it does for enclosures in 501.3(A), for example.
Since you haven't yet demonstrated a need for flexibility [501.4(B)(2)], technically liquid tight would still be a violation. Here is where reason needs to step in. With the additional proviso of installing the liquid tight per 501.16(B), I think this would be a good application of 90.4.