sara1011@optonline.net
Member
- Location
- woodridge new jersey
for hot tubs and spas ....why, for the love of saint frances, can sealtite only be 6 ft long max????????????????????????????
sara1011@optonline.net said:for hot tubs and spas ....why, for the love of saint frances, can sealtite only be 6 ft long max????????????????????????????
Run it 5'11" then change to EMT then back to flex. Just kidding.paul said:Cus 680.42(A)(1) says so.
680.42 Outdoor Installations
A spa or hot tub installed outdoors shall comply with the provisions of Parts I and II of this article, except as permitted in 680.42(A) and 680.42
(1) Flexible Conduit Liquidtight flexible metal conduit or liquidtight flexible nonmetallic conduit shall be permitted in lengths of not more than 1.8 m (6 ft).
roger said:680.42 (A)(1)
350.30 isn't applicable, it has been modified in 680.42
Roger
sara1011@optonline.net said:as was asked previously.........does any one know why?????????!!!!!!!! (thx trevor you re apparently the only one who read my inquiry)
sara1011@optonline.net said:as was asked previously.........does any one know why?????????!!!!!!!! (thx trevor you re apparently the only one who read my inquiry)
RayS said:Can't say as I know the answer either, but I offer a guess:
to limit possibility for mechanical damage exposing conductors (especially to the sharp metal)
roger said:Kingpb, I don't think anybody in this thread thought there was a length limit to LFMC or LFNMC in chapter 1 through 4 applications but, when these chapters are suplemented or modified by chapters 5,6,or 7 we are in a different ball game.
Roger
the metal ya get when ya crush metallic flex. I know, the original post was for both types...kingpb said:What sharp metal?
kingpb said:I would expect then to see 680, and other sections modified to correct the 6' max length issue.
17-139 Log #560 NEC-P17
Final Action: Reject
(680.42)
____________________________________________________________
Submitter:Brian Magilley, Current Electric
Recommendation:Delete the following text:
680.42(A)(1) Flexible Conduit. Liquidtight flexible metal conduit or
liquidtight flexible nonmetallic conduit shall be permitted in lengths of not
more than 1.8 m (6 ft).
Substantiation:I do not see what purpose this 6 foot limitation serves. I feel
that removing this section will allow for easier connection of the spa to the
required disconnect. If I set the required disconnect 5 feet from the edge of a
residential spa then I cannot run LFNMC the entire length from the disconnect
to the spa without using two different conduit types. Having the option of
running an unlimited length of LFNMC from the spa disconnect 5 feet away to
the spa control panel, would make the installation much quicker than having to
run say PVC (RNMC) from the disconnect up to the spa, and then make a
transition over the LFNMC to the spa control panel.
Panel Meeting Action: Reject
Panel Statement:
Other wiring methods are permitted precluding the use of
LFMC.
Number Eligible to Vote: 11
Ballot Results:
Affirmative: 11
Comment on Affirmative:
BLEWITT, T.: UL Guide Information for LFMC specifies the length
limitation when the metal jacket is part of the equipment grounding path:
?Where terminated in fittings investigated for grounding and where installed
with not more than 6 ft (total length) in any ground return path, liquid-tight
flexible metal conduit in the 3/8 and 1/2 (12 and 16) trade sizes is suitable for
grounding where used on circuits rated 20 A or less, and the 3/4, 1 and 1-1/4
(21, 27 and 35) trade sizes are suitable for grounding where used on circuits
rated 60 A or less.? Also see 250.118(5).
Final Action: Reject
(680.42(A)(1))
____________________________________________________________
Submitter:Mike Wilson, Mike Wilson Electrical Service / Rep. Wake County
Electrical Contractors Association
Recommendation:Revise text to read:
Flexible Conduit. Liquidtight flexible metal conduit or liquidtight flexible
nonmetallic conduit shall be permitted in lengths of not more than 1.8 m (6 ft) .
Substantiation:Flex that is 6 ft is not long enough to run from a control panel
under the tub to a disconnect (5 ft) away. The tub is manufactured in an entry
on the left side. Control panel is (4 ft) from the side of the (text unreadable by
NFPA staff). A disconnect could not be (text unreadable by NFPA staff) using
(6 ft) of flex.
Panel Meeting Action: Reject
Panel Statement:
Other wiring methods are permitted precluding the use of
LFMC.
Number Eligible to Vote: 11
Ballot Results:
Affirmative: 11
Comment on Affirmative:
BLEWITT, T.: UL Guide Information for LFMC specifies the length
limitation when the metal jacket is part of the equipment grounding path:
? Where terminated in fittings investigated for grounding and where installed
with not more than 6 ft (total length) in any ground return path, liquid-tight
flexible metal conduit in the 3/8 and 1/2 (12 and 16) trade sizes is suitable for
grounding where used on circuits rated 20 A or less, and the 3/4, 1 and 1-1/4
(21, 27 and 35) trade sizes are suitable for grounding where used on circuits
rated 60 A or less.? Also see 250.118(5).