List of conductors you can and can't phase?

Location
Idaho
Occupation
Apprentice
Afternoon,

Wanting to create a list of conductors that you can and can not phase. Wanting to keep it simple.

Conductors that you can phase:

-Grounded conductors in a cable assembly (10/3 Romex, neutral phased as an ungrounded conductor.
-Ungrounded conductors of any kind
-Conductors 4 AWG and larger

Conductors you can not phase:

-Conductors 6 AWG and smaller
-Grounded condcutors
-???

Thank you!
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Note that these rules only apply to conductors used as grounded conductors or EGCs. Ungrounded conductors of any size can be re-identified.
 