If one installs a combination afci/gfi receptacle, what would be the listed breaker combination if for example the device is leviton
No, unlike GFCI's these AFCI are being triggered by upstream and utility side events.Unless I am missing some thing. It's no different then when you install a gfci outlet , It's all protected down side of your outlet.
As RJ said, just because they do it, doesn't mean squat if not listed by testing standard for doing it correctly, as intended by the standard.the key word being 'listed'........~RJ~
Okay, so I was missing some thing. Been in Indiana to long ... Come on man ...No, unlike GFCI's these AFCI are being triggered by upstream and utility side events.
As RJ said, just because they do it, doesn't mean squat if not listed by testing standard for doing it correctly, as intended by the standard.
I think you are referring to 210.12(4). As I recall no one ever made a breaker that was listed for this even tough it was written into the code.If one installs a combination afci/gfi receptacle, what would be the listed breaker combination if for example the device is leviton
I don't believe that there is a completed standard that such a breaker can be listed to.I was surprised that when Leviton introduced their own brand of loadcenter they didn't come up with a "listed" breaker to be used with their AFCI receptacle to meet that requirement.
Not in the NEC. Maybe a state amendment from where the person who answered the question is located?Someone else at Leviton customer support emailed me this morning.
"Please see below regarding 210.12.A4:"
"Exception No 4: AFCI protection shall not be required for branch circuits that serve an appliance that is not easily moved or that is fastened in place."
Does such an exception exist with 2020 NEC?. Can't find it with the 2017 NEC.
As I recall, that is the case. I recall having this discussion with the UL guys some time back.I don't believe that there is a completed standard that such a breaker can be listed to.
I sent in a comment to remove it-- I lost...hahahaThis is just part of the code fight between the breaker manufacturers and the device manufacturers. If you go back and look at the vote on the floor motion to keep this in the code a cycle or two ago, you will find that there were about twice as many people voting on the motion to keep the rule in the code as there were on any of the other motions made that day.
There is no device on the market that will permit this.
LOL... as in lot's of luck.I sent in a comment to remove it-- I lost...hahaha
That change did pass at the panel level for the 2017 code, but was reversed at the NFPA meeting. It appears that the meeting was "packed" as there were almost twice as many floor votes cast on the motion than on any of the other motions to change what the code making panels did.I sent in a comment to remove it-- I lost...hahaha
Wow, that is unbelievable. So it is true that the manufacturers control much of the code....That change did pass at the panel level for the 2017 code, but was reversed at the NFPA meeting. It appears that the meeting was "packed" as there were almost twice as many floor votes cast on the motion than on any of the other motions to change what the code making panels did.
Shades of "Allied Tube V Indian Head" where the packing of the NFPA meeting to vote down ENT kept that product out of the code for an additional 3 years. In that case, the steel tube people paid employees to join the NFPA and go to the meeting and vote a competitive product out of the code. That case resulted in a rule that requires you must be an NFPA member for at least 180 day before being permitted to vote on any motions at the meeting.
this is an epiphany Den?Wow, that is unbelievable. So it is true that the manufacturers control much of the code....