Bugeatersmn
Member
- Location
- Minnesota
- Occupation
- Electrician
Journeyman electrician for 8 years now, I'm in the process of helping a Bible camp plan for an addition of some new dwellings. They were going to run a 200 amp, 120/208 feeder to a main panel, then have breakers for the individual cabins on that panel using 2 of the 3 phases for each cabin. I told them they could save the cost of that panel by having a junction box and just tap off of the feeder in there and feed individual disconnects within the NEC tap rules. A setup which I'm willing to donate and prep. I was able to get a large type 4 enclosure as well as distribution blocks (all brand new components) for less than $400. The director is telling me that the inspector told the electrician who pulls their permits and oversees the projects, that the enclosure won't be UL listed for that purpose. The components are listed, but the assembly won't be. This isn't a control cabinet or a new piece of equipment, it's just a big junction box. Insulated multiport taps would be 100% legal, but not listed distribution blocks? Any inspectors out there able to weigh in on this? Thanks.