Found One in article 695. I think that's it.
Dennis,
Have YET to find anywhere that Underwriter's Lab (U.L.)
is specifically linked with 'Listed" or "Listing" or "approved".
But, it is obvious that the implied authority is from U.L.
or C.S.A. or ANSI, etc.
***(1) Searched for terms like these:
UL
CSA
ANSI
Listing
***(2) Found these cites for starters:
Intro:
This Code is purely advisory as far as NFPA is concerned
100:
FPN: Some examples of ways to determine suitability of
equipment for a specific purpose, environment, or application
include investigations by a qualified testing laboratory
(listing and labeling), an inspection agency, or other organizations
concerned with product evaluation.
100:
Listed. Equipment, materials, or services included in a list
published by an organization that is acceptable to the authority
having jurisdiction and concerned with evaluation
of products or services, that maintains periodic inspection
of production of listed equipment or materials or periodic
evaluation of services, and whose listing states that either
the equipment, material, or service meets appropriate designated
standards or has been tested and found suitable for
a specified purpose.
FPN: The means for identifying listed equipment may vary
for each organization concerned with product evaluation,
some of which do not recognize equipment as listed unless
it is also labeled. Use of the system employed by the listing
organization allows the authority having jurisdiction to
identify a listed product.
110.3 Examination, Identification, Installation,
and Use of Equipment.
(A) Examination. In judging equipment, considerations
such as the following shall be evaluated:
(1) Suitability for installation and use in conformity with
the provisions of this Code
FPN: Suitability of equipment use may be identified by a
description marked on or provided with a product to identify
the suitability of the product for a specific purpose,
environment, or application. Suitability of equipment may
be evidenced by listing or labeling.
(B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.
110.10 Circuit Impedance and Other Characteristics.
Listed products applied in accordance with their listing
shall be considered to meet the requirements of this section.
***(3) Leads me to believe that the AHJ is literally the AHJ !