Now that I have your attention, I stumbled into a big black hole during a Bonding & Grounding class I gave recently at a hamfest. A relatively large class, I knew several attendees professionally and personally as they are both Hams and electrical contractors I have worked with for decades,
As I covered article 810, exceptionally 810.57 requiring a listed ADU, John, a contractor I have worked with for decades, interrupted and informed me it was BS. He was right. Impossible to comply with. There is no such thing as a Listed ground block or ADUs used by radio operators. I was stunned and asked how we got away with it for decades and hundreds of inspections. No one checks or cares when a PE stamp is involved, I own the responsibility if something happens. No UL-listed ground blocks or ADUs are manufactured for radio operators I am aware of.
Walking into any box store or supply house, you will find hundreds of ground blocks and ADUs for CATV using 75-ohm coax and “F” type Coax connectors stamped with UL-452. Radio transmitter and receivers do not use “F” type CATV Coax Connectors, operate at much higher power levels, and is 50-ohms.
I use high-end Industrial equipment from manufacturers like CommScope and PolyPhaser, who make HEMP-rated ADUs for the military and all ADUs for cellular and commercial users. They have all kinds of listings, standards, and certifications. All have CE, MIL-STD, and IEC ratings; none have UL. I know CE will not cut the mustard, perhaps IEC?
Not sure if there is a correct answer or not. I know I have to change course material and am not comfortable saying, ignore the code, do not pull a permit, buy a quality ADU, and do the best you can. It is impossible to comply.
Any Inspectors out there. All comments are welcome.
As I covered article 810, exceptionally 810.57 requiring a listed ADU, John, a contractor I have worked with for decades, interrupted and informed me it was BS. He was right. Impossible to comply with. There is no such thing as a Listed ground block or ADUs used by radio operators. I was stunned and asked how we got away with it for decades and hundreds of inspections. No one checks or cares when a PE stamp is involved, I own the responsibility if something happens. No UL-listed ground blocks or ADUs are manufactured for radio operators I am aware of.
Walking into any box store or supply house, you will find hundreds of ground blocks and ADUs for CATV using 75-ohm coax and “F” type Coax connectors stamped with UL-452. Radio transmitter and receivers do not use “F” type CATV Coax Connectors, operate at much higher power levels, and is 50-ohms.
I use high-end Industrial equipment from manufacturers like CommScope and PolyPhaser, who make HEMP-rated ADUs for the military and all ADUs for cellular and commercial users. They have all kinds of listings, standards, and certifications. All have CE, MIL-STD, and IEC ratings; none have UL. I know CE will not cut the mustard, perhaps IEC?
Not sure if there is a correct answer or not. I know I have to change course material and am not comfortable saying, ignore the code, do not pull a permit, buy a quality ADU, and do the best you can. It is impossible to comply.