Having a brain fart,
when listing for example a everyday 4500 watt water heater or any appliance which utilizes 2poles do you list the full wattage on both A column and B column (ex. 4500 on A and 4500 on B) or should I be splitting the wattage across the two phases (ex. 2250 on A and 2250 on B so the total =4500) something doesn't seem to jive when taking a total for one column and dividing by 120 volts to get amperage per phase, seems to high.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
For any line-to-line load you allocate half the VA to one leg and half to the other.
This will give you a more correct line current on each leg when you add the VA up and apply either the single phase or three phase power to amperage conversion as appropriate.
 